In the proma manual is says it “uses inputs of outermost connectors LIMIT OR HOME - THC relay contacts should be connected to the terminals the same way as limit switches connectors.”
What are your thought? This is out of the proma manual they sent me
This is BAD writing on behalf or Proma - it has NOTHING to do with limits at all.
From the manual....
The relay outputs “Arc, Up, Down”, are controlling outputs via relays, and should not be utilized for anything other then it's intended use.
COM terminal is a common input terminal connected to the ARC, UP and DOWN relay contacts inside the device, according to the diagram located on the cover (above picture). Suggested route is to “GND” at driver/pc end. Do not jumper this connection to the “7-35V” negative.
ARC output (also known as “Arc Okay”) is activated when plasma ignition is detected. Route and configure for a software input. Not required to operate.
UP output is activated when the measured voltage is lower than the voltage setpoints, reduced by half the hysteresis voltage. Route and configure for a software input.
DOWN output is activated when the measured voltage is higher than the voltage setpoints, reduced by half the hysteresis voltage. Route and configure for a software input.
Note: No output relays are activated in case when only the pilot arc is detected and when the main arc is broken.
SO, you need to connect the ARC, UP, DOWN to suitable free inputs on your BOB, then connect the COM to whatever your BOB needs - +5 or 0v etc.
Next configure Mach3 inputs to recognise the input signals from the PROMA.
Now, put the PROMA into test mode - this just sends repeat UP & DOWN outputs to Mach - make sure your Z axis responds in the correct direction, if not, fix it in settings. You may need to set temporarily in Mill options, ports and pins - allow THC moves when not in THC mode to let the z move without an Arc OK signal.
Next connect your plasma - are your using HIGH voltage inputs or LOW voltage inputs?

??