0.8Kw water spindle running with 2.2Kw VFD
« on: November 26, 2010, 03:10:27 PM »
Hi,

Is there any problem running a 0.8Kw water cooled spindle with a 2.2Kw VFD.

Just ordered a 0.8Kw water cooled spindle and I have a spare 2.2Kw VFD both bought from love-happyshopping on Ebay.

I have put a picture of the VFD in case.

Thanks for your time, Jeff

Offline Sam

*
  • *
  •  987 987
    • View Profile
    • hillbillyhilton.com
Re: 0.8Kw water spindle running with 2.2Kw VFD
« Reply #1 on: November 26, 2010, 04:54:55 PM »
Usually, this is not a problem. There should be parameters in the VFD that you match up to the motor. It's pretty common to get a higher rated VFD to accommodate a motor upgrade in the future. I do not know anything about the Huanyang stuff.
"CONFIDENCE: it's the feeling you experience before you fully understand the situation."
Re: 0.8Kw water spindle running with 2.2Kw VFD
« Reply #2 on: November 26, 2010, 05:07:59 PM »
Hi, that's what I tough.

I think that 142 is the parameter to be set at 5 to 6 amp for a 0.8 KW motor.


Thanks a lot, Jeff
Re: 0.8Kw water spindle running with 2.2Kw VFD
« Reply #3 on: November 27, 2010, 11:56:26 AM »
I've also done it the other way round -
3kw inverter driving a 5kw motor - it just llimits the max grunt out I can get out of the motor.

(Siemens inverter)
ATB
Derek
You can "chop it off" but can't "chop it on"