Hello Guest it is October 22, 2026, 04:25:26 PM
Author Topic: Modbus communications problew  (Read 5597 times)
« on: April 21, 2019, 06:33:57 PM »
Having an issue setting up modbus communications between Mach4 and PLC. I can write multiple holding registers from Mach to the PLC but cannot read any.
I have Mach4 installed on a computer and connected to a compactlogix PLC via Prosoft MVI69-MNET card via ethernet
PC IP address 192.168.1.40
Mach 4 modbus configured for TCP, IP address 192.168.1.48
1)   read register 50, 10 words long
2)   write register 1, 10 words long
MNET IP 192.168.1.48  - read/write to IP address 192.168.1.40
1)   writes to holding register 50, 10 words long
2)   Reads holding register 1, 10 words long
In my PLC data table I can see signals from Mach4 eg. Axis enable bits, but when I set a bit in the PLC that would jog an axis, the bit is not seen in Mach.
If I run a modbus simulator on the computer I see data from both in the correct registers.
As a side note, if I change the Mach modbus configuration to IP address of the computer with the modbus simulator running, I get 2 way communications.
What is wrong with me setup? I should not need to run a simulator.
Re: Modbus communications problew
« Reply #1 on: April 23, 2019, 04:54:12 AM »
The fact that you can read data from the PLC that was written there by Mach certainly proves communication at least from
Mach to the PLC. I would guess then that the reverse is true, that is there must be communication between the PLC back
to Mach, Ethernet comms REQUIRES a bidirectional link.
Where abouts 'in Mach' are you looking for the data supposedly transmitted by the PLC?
My understanding is that ALL data, whether it be out-going or in-coming all have registers to hold it.
Are there any registers owned by the Modbus Plugin that correspond to the incoming data packets?
« Last Edit: April 23, 2019, 04:56:08 AM by joeaverage »