Hello Guest it is October 24, 2026, 03:32:17 PM
Author Topic: how to wire PNOZ X7 with drivers MR-J2S-60A and CSMIO-IP-A  (Read 47874 times)
Re: how to wire PNOZ X7 with drivers MR-J2S-60A and CSMIO-IP-A
« Reply #10 on: April 18, 2014, 09:45:41 AM »
Not sure what you are asking, or are you just stating your thoughts?
« Reply #11 on: April 18, 2014, 09:46:43 AM »
BTW my above post should have been +24v instead of _24v
Offline sdow
  •  67 67
« Reply #12 on: April 18, 2014, 10:36:59 AM »
if you see your picture with connection PNOZ .... only one wire from drivers go to Pnoz   ....  i my situation can i connect  4 faults in the same input of PNOZ
« Last Edit: April 18, 2014, 10:44:01 AM by sdow »
Offline sdow
  •  67 67
« Reply #13 on: April 18, 2014, 11:02:07 AM »
is that ok ? how i connect the faults outputs
« Reply #14 on: April 18, 2014, 02:24:12 PM »
Do your drives output 24v when there is a fault or do they remove the 24v output?
Offline sdow
  •  67 67
« Reply #15 on: April 18, 2014, 03:46:54 PM »
look the second picture   when was the fault (ALM) it activate just a transistor
« Last Edit: April 18, 2014, 03:54:16 PM by sdow »
« Reply #16 on: April 18, 2014, 05:23:35 PM »
Ok, not the sharpest when it comes to electronics but it looks to me as if the output sinks. If that is the case then you could use the relay but it would have to be different. What you would have to do is have 24v going to the relays coil and the other side of the coil would connect to each of the fault outputs on your drive, you would then need to use the NC contact of the relay rather than the NO that you seem to be showing.
So what would happen is the coil is fed by 24v but it would not connect to 0v  until one of the drives faulted. So in a Non-Fault position the 24v connected to the relays contacts would pass through the NC contact and onto the E-Stop string. If one drive faulted then the coil would get powered and the relays contact would open and thus the E-Stop string would be opened thus signalling an e-stop.
Offline sdow
  •  67 67
« Reply #17 on: April 19, 2014, 08:25:54 AM »
can put the parameter in CS-MIO   that fault is activated as LOW   .... and do that
Offline sdow
  •  67 67
« Reply #18 on: April 19, 2014, 02:49:41 PM »
i see in this picture  we can connect many faults to the in CS-MIO-A ... i not see where i need to connect it on the port inputs 0-11 and how configure that  ....if is 0 on input 1 ,2 or 3  ....all motors need to stop
« Reply #19 on: April 20, 2014, 05:55:06 PM »
You can wire things any way you wish and makes sense for you. The diagram CS-Lab has in the manual is just a way they suggest it can be done and I was thinking you were wishing to do it that way and thus I tailored my answers to that.
Below are two ways I do it with different drives and different machines using different safety relays.