Author Topic: External Estop Requested  (Read 9327 times)

0 Members and 1 Guest are viewing this topic.

Offline Hood

*
  •  25,835 25,835
  • Carnoustie, Scotland
    • View Profile
Re: External Estop Requested
« Reply #10 on: April 23, 2013, 01:46:12 PM »
Doesnt sound normal to me, check your wiring to make sure there is no breakdown in the isolation of the wires.
If not then could well be internal insulation that is breaking down. Not sure if it is safe to test a stepper with a megger or not, dont see why not but wouldnt like to say for sure. If it is safe and you did get one to test then that would tell you if the insulation in the motor is breaking down.
Hood

Offline djk

*
  •  13 13
    • View Profile
Re: External Estop Requested
« Reply #11 on: April 23, 2013, 03:31:30 PM »
These motors were bought two years ago new and wired up for testing a week ago ???
Sanyo Denki $$$  :'(

Offline Hood

*
  •  25,835 25,835
  • Carnoustie, Scotland
    • View Profile
Re: External Estop Requested
« Reply #12 on: April 23, 2013, 04:21:28 PM »
Shouldnt be the motors then, well suppose you can never say never but Sanyos are good motors so its unlikely. Check your wiring thoroughly and if its not that then it may be the drives.
Hood

Offline djk

*
  •  13 13
    • View Profile
Re: External Estop Requested
« Reply #13 on: April 24, 2013, 10:54:28 AM »
Tested one of the motors its ok. the stepper drives are at fault?

Thanks for your help

David

Offline Hood

*
  •  25,835 25,835
  • Carnoustie, Scotland
    • View Profile
Re: External Estop Requested
« Reply #14 on: April 24, 2013, 02:41:43 PM »
something definitely sounds amiss, where the problem is I wouldnt like to say but it does seem you have some sort of leak to earth.
Hood

Offline djk

*
  •  13 13
    • View Profile
Re: External Estop Requested
« Reply #15 on: April 26, 2013, 03:48:14 AM »
Ripped every thing out of my control box and tested the drives.
I have 100VAC on the earth and 230V on R+ of the motor connection. ( the 3 drives )

Offline Hood

*
  •  25,835 25,835
  • Carnoustie, Scotland
    • View Profile
Re: External Estop Requested
« Reply #16 on: April 26, 2013, 08:28:31 AM »
Where are you measuring this voltage, earth to frame of drive?
Hood

Offline djk

*
  •  13 13
    • View Profile
Re: External Estop Requested
« Reply #17 on: April 26, 2013, 09:33:48 AM »
Earth mains to earth of the driver (PE)
The driver is on a wooden board pluged in to the mains no motors or BOB

Offline Hood

*
  •  25,835 25,835
  • Carnoustie, Scotland
    • View Profile
Re: External Estop Requested
« Reply #18 on: April 26, 2013, 01:27:32 PM »
That certainly doesnt sound right to me, quite dangerous in fact.
Hood

Offline stirling

*
  • *
  •  2,188 2,188
  • UK
    • View Profile
    • www.razordance.co.uk
Re: External Estop Requested
« Reply #19 on: April 26, 2013, 01:34:27 PM »
If you are correct (not suggesting you aren't) and you have 100Vac on the PE (earth) connection of your driver and if the driver is in a metal case (which hopefully it is) then I assume you have 100Vac on the case too. This is generally not a good thing.

As far as you're thread title goes - personally I'd say that's the least of your problems. If it were me I'd turn that puppy off right now. Zapp Auto sell them so it may be worth having a chat with them, but my guess FWIW is they're a) banjaxed and b) dangerous.

Ian