Hello Guest it is October 24, 2026, 02:51:44 PM
Author Topic: touch probe function question  (Read 35567 times)
Re: touch probe function question
« Reply #20 on: July 12, 2019, 11:49:28 AM »
Got it.  Mach support never got back to me on my ticket request.  I will try again and this time attach the log file from my most recent attempt to probe Z
« Reply #21 on: July 12, 2019, 03:35:11 PM »
Sorry, just seeing this.
Finding Z should work exactly as you expect. But one thing that will break the functionality is a noisy or bouncy probe input. Ensure that is not a problem. Lots of info here to help with that.
All moves but one are actually probe moves so if something triggers the probe, motion stops. However that safety comes with one caveat. The retract move can't be a probe move because you can't start a probe move if the probe is active. So, if after retract the input is still active you see what you are seeing. Why would the retract move need to be bigger? Because when you do a probe move the exact position the probe triggered is stored and that is what sets the coordinates. However, after the input goes active the axis has to stop respecting the accel/decel in motor tuning so the tool tip will be beyond the position it touched. How much will vary depending on touch rate, motor tuning backlash, etc.. So, make your retract distance bigger and retest, lower touch rate, etc. It may take a bit of tuning to get it all dialed in for your machine.
« Reply #22 on: July 12, 2019, 03:39:30 PM »
Meant to say too............
The TouchOff module isn't that bad. A lot of it is the embedded button images. But most functions are just running other functions in a particular order. In a nutshell it all boils down to just a few moves (prep move, touch move, retract move) that has some variables.
« Reply #23 on: July 12, 2019, 05:52:24 PM »
As far as bounce is concerned, I am just using a simple plate and an aligator clip on the bit.  Not sure how I could do anything directly with bounce in that arrangement.
As far as retract distance, I am trying to retract 5mm.  Is that not enough?
I figured out that two thirds of the file was image data.  I was not completely sure what is the main function that pulls it all together.  i will give it another look, but from what you're telling me, it sounds line a timing issue more than anything.  Am I wrong?   Without knowing the code very well, is it possible that there could be a place in the functions that I might add a 100 ms delay to let any bounce settle down?  (not even sure if lua has a delay function) If so, which function should I be looking at to place a delay into.
« Reply #24 on: July 12, 2019, 06:18:30 PM »
the 'bounce' chaoticone is referring to is electrical double operation and/or noise on the probe circuit.
Try increasing the debounce or input filtering on your probe signal line. A substantial capacitor (0.1uf -1 uF)
on the input is another worth while experiment.
« Reply #25 on: July 13, 2019, 10:35:05 AM »
I know what bounce is.  The problem I have is that i am using a simple aluminum plate and alligator clips (ground and v+) so there is no adjustment.  I know this is not a unusual arangement (per several youtube videos).  Are you saying that this sort of simple probe won't work for what I am trying to do?   I am not trying to be obtuse.  I just don't understand.
« Reply #26 on: July 13, 2019, 01:02:49 PM »
Ok, being the dummy that I am, it took me a while to understand about the filtering. When I looked at it, there was no filtering at all (0), I bumped the filtering up to 1000 and tried again.  Same result.  Bumped it to 2000.  Same result.  I am not sure how high I should go. The log file for these two attempts is below if that tells anyone anything usefull.
Code: [Select]
2019-07-13 13:50:10.480 - Loggging Enabled.
2019-07-13 13:50:22.216 - API: mcCntlEnable(true) called.
2019-07-13 13:50:22.217 - Signal id 1019, (Enable #1), changed from LOW to HIGH.
2019-07-13 13:50:22.217 - Signal id 1021, (Enable #3), changed from LOW to HIGH.
2019-07-13 13:50:22.217 - Signal id 1020, (Enable #2), changed from LOW to HIGH.
2019-07-13 13:50:22.218 - Signal id 1120, (Machine Enabled), changed from LOW to HIGH.
2019-07-13 13:50:30.719 - API: mcCntlGcodeExecute() called. (G91 G31 Z -5.25F5)
2019-07-13 13:50:30.919 - Attempt transition from "Idle" on event "MDI Start" Controller.cpp:1811
2019-07-13 13:50:30.919 - S_IDLE_on_exit
2019-07-13 13:50:30.919 - ACTION_start_mdi
2019-07-13 13:50:30.919 - S_MDI_RUNNING_on_entry
2019-07-13 13:50:30.919 - S_MDI_RUNNING2_on_entry
2019-07-13 13:50:30.920 - Signal id 1114, (Gcode Running), changed from LOW to HIGH.
2019-07-13 13:50:30.936 - Attempt transition from "MDI Running" on event "Probe" RunCanon.cpp:497
2019-07-13 13:50:30.936 - S_MDI_RUNNING2_on_exit
2019-07-13 13:50:30.936 - Signal id 1114, (Gcode Running), changed from HIGH to LOW.
2019-07-13 13:50:30.936 - ACTION_start_probe
2019-07-13 13:50:30.937 - >>>>> ESS Probe 0, Starting.
2019-07-13 13:50:30.938 - S_MDI_PROBING_on_entry
2019-07-13 13:50:30.938 - Probing: Waiting on exit event... RunCanon.cpp:236
2019-07-13 13:50:30.938 - Controller::RunCanonBuffer called AddStopReportRequest() RunCanon.cpp:76
2019-07-13 13:50:30.938 - Requesting a stopped report for axis 0 motors.
2019-07-13 13:50:30.938 - Requesting a stopped report for motor 0.
2019-07-13 13:50:30.938 - Requesting a stopped report for axis 1 motors.
2019-07-13 13:50:30.938 - Requesting a stopped report for motor 1.
2019-07-13 13:50:30.938 - Requesting a stopped report for motor 3.
2019-07-13 13:50:30.938 - Requesting a stopped report for axis 2 motors.
2019-07-13 13:50:30.938 - Requesting a stopped report for motor 2.
2019-07-13 13:50:30.939 - Waiting on SetStill...
2019-07-13 13:50:30.960 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 0
2019-07-13 13:50:30.960 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 1
2019-07-13 13:50:30.960 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 2
2019-07-13 13:50:30.960 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 3
2019-07-13 13:50:30.960 - >>>>ESS: Switching from NORMAL to PROBE state for Probe 0
2019-07-13 13:50:31.510 - -----ESS: Checking for Probe0 Strike, none yet...
2019-07-13 13:50:32.060 - -----ESS: Checking for Probe0 Strike, none yet...
2019-07-13 13:50:32.360 - Signal id 161, (PROBE), changed from LOW to HIGH.
2019-07-13 13:50:32.360 - -----ESS: Mach ACKs Probe0 input signal ON!
2019-07-13 13:50:32.361 - API: mcMotionSetProbePos() called. motor 0 position 0.0000
2019-07-13 13:50:32.361 - API: mcMotionSetProbePos() called. motor 1 position 0.0000
2019-07-13 13:50:32.361 - API: mcMotionSetProbePos() called. motor 2 position -54.0000
2019-07-13 13:50:32.361 - API: mcMotionSetProbePos() called. motor 3 position 0.0000
2019-07-13 13:50:32.361 - API: mcMotionSetProbePos() called. motor 4 position 0.0000
2019-07-13 13:50:32.361 - API: mcMotionSetProbePos() called. motor 5 position 0.0000
2019-07-13 13:50:32.361 - ^^^^^^ ESS: Success! Probe0 Strike. Switching from PROBING to PROBING_CLEANUP state.
2019-07-13 13:50:32.410 - ^^^^^^ ESS Probe0 Finished: The device is still and the buffer is empty.
2019-07-13 13:50:32.410 - API: mcMotionClearPlanner() called.
2019-07-13 13:50:32.410 - API: mcMotionSetProbeComplete() called.
2019-07-13 13:50:32.410 - Recording latched probe positions.
2019-07-13 13:50:32.411 - Attempt transition from "Probing" on event "Probe Complete" MachAPI.cpp:1348
2019-07-13 13:50:32.411 - S_MDI_PROBING_on_exit
2019-07-13 13:50:32.411 - ACTION_stop_probe
2019-07-13 13:50:32.411 - >>>>> ESS Probe 0, Done
2019-07-13 13:50:32.413 - S_MDI_RUNNING2_on_entry
2019-07-13 13:50:32.413 - Signal id 1114, (Gcode Running), changed from LOW to HIGH.
2019-07-13 13:50:32.415 - SyncPosition()! Clearing planner.
2019-07-13 13:50:32.415 - .^^^^^ESS: Switching from PROBING_CLEANUP to NORMAL state.
2019-07-13 13:50:32.415 - Waiting on SetStill is Done!
2019-07-13 13:50:32.415 - Probing: Exiting hold because of probe strike. GcodeExec.cpp:1272
2019-07-13 13:50:32.535 - Attempt transition from "MDI Running" on event "Stop" GcodeExec.cpp:1099
2019-07-13 13:50:32.535 - S_MDI_RUNNING2_on_exit
2019-07-13 13:50:32.535 - Signal id 1114, (Gcode Running), changed from HIGH to LOW.
2019-07-13 13:50:32.535 - S_MDI_RUNNING_on_exit
2019-07-13 13:50:32.535 - ACTION_stop
2019-07-13 13:50:32.560 - Signal id 161, (PROBE), changed from HIGH to LOW.
2019-07-13 13:50:32.562 - S_IDLE_on_entry
2019-07-13 13:50:32.562 - -----ESS: Mach ACKs Probe0 input signal OFF.
2019-07-13 13:50:32.623 - API: mcCntlGcodeExecute() called. (G 91
F 5)
2019-07-13 13:50:32.823 - Attempt transition from "Idle" on event "MDI Start" Controller.cpp:1811
2019-07-13 13:50:32.823 - S_IDLE_on_exit
2019-07-13 13:50:32.823 - ACTION_start_mdi
2019-07-13 13:50:32.823 - S_MDI_RUNNING_on_entry
2019-07-13 13:50:32.823 - S_MDI_RUNNING2_on_entry
2019-07-13 13:50:32.824 - Signal id 1114, (Gcode Running), changed from LOW to HIGH.
2019-07-13 13:50:32.846 - API: mcCntlEStop() called.
2019-07-13 13:50:32.846 - API: mcCntlEnable(false) called.
2019-07-13 13:50:32.846 - API: mcCntlCycleStop() called.
2019-07-13 13:50:32.847 - Signal id 1019, (Enable #1), changed from HIGH to LOW.
2019-07-13 13:50:32.847 - Signal id 1021, (Enable #3), changed from HIGH to LOW.
2019-07-13 13:50:32.847 - Attempt transition from "MDI Running" on event "Stop" MachAPI.cpp:2678
2019-07-13 13:50:32.847 - S_MDI_RUNNING2_on_exit
2019-07-13 13:50:32.847 - Signal id 1114, (Gcode Running), changed from HIGH to LOW.
2019-07-13 13:50:32.847 - Signal id 1020, (Enable #2), changed from HIGH to LOW.
2019-07-13 13:50:32.848 - Attempt transition from "MDI Running" on event "Stop" Controller.cpp:4535
2019-07-13 13:50:32.848 - S_MDI_RUNNING_on_exit
2019-07-13 13:50:32.848 - Signal id 1120, (Machine Enabled), changed from HIGH to LOW.
2019-07-13 13:50:32.848 - ACTION_stop
2019-07-13 13:50:32.848 -    $$$ ESS: Mach4 was Disabled - Force Output Stop Sates Now
2019-07-13 13:50:32.848 -    !!! ESS: Stop Event IGNORING command to turn OFF DISABLED output Port1-Pin14 - Spindle ON Relay
2019-07-13 13:50:32.848 -    $$$ ESS: Finished processing the Stop Event
2019-07-13 13:50:32.872 - S_IDLE_on_entry
2019-07-13 13:50:32.937 - Attempt transition from "Idle" on event "Stop" GcodeExec.cpp:1099
2019-07-13 13:50:32.937 - Can't transition from "Idle" on event "Stop"
2019-07-13 13:54:07.881 - -----ESS: Switching from NORMAL to CONFIG state
2019-07-13 13:54:40.889 - ESS Called its Reconfigure() function
2019-07-13 13:54:40.911 - ESS: Switching from CONFIG to NORMAL state
2019-07-13 13:54:46.193 - API: mcCntlEnable(true) called.
2019-07-13 13:54:46.193 - Signal id 1019, (Enable #1), changed from LOW to HIGH.
2019-07-13 13:54:46.194 - Signal id 1021, (Enable #3), changed from LOW to HIGH.
2019-07-13 13:54:46.194 - Signal id 1020, (Enable #2), changed from LOW to HIGH.
2019-07-13 13:54:46.194 - Signal id 1120, (Machine Enabled), changed from LOW to HIGH.
2019-07-13 13:54:57.194 - API: mcJogVelocityStart() called. Axis 2, dir = 1
2019-07-13 13:54:57.194 - Attempt transition from "Idle" on event "Jog" Axis.cpp:632
2019-07-13 13:54:57.194 - S_IDLE_on_exit
2019-07-13 13:54:57.194 - ACTION_start_jogging
2019-07-13 13:54:57.194 - S_JOGGING_on_entry
2019-07-13 13:54:58.362 - API: mcJogVelocityStop() called. Axis 2
2019-07-13 13:54:58.915 - Requesting a stopped report for axis 2 motors. Axis.cpp:806
2019-07-13 13:54:58.915 - Requesting a stopped report for motor 2.
2019-07-13 13:54:58.915 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 2
2019-07-13 13:54:59.114 - All motors marked as still.
2019-07-13 13:54:59.114 - Main planner updated from last mcMotionSetPos().
2019-07-13 13:54:59.114 - Attempt transition from "Jogging" on event "Stop Jog" Controller.cpp:1076
2019-07-13 13:54:59.115 - S_JOGGING_on_exit
2019-07-13 13:54:59.115 - S_FILE_RUNNING_stop_jogging
2019-07-13 13:54:59.115 - S_IDLE_on_entry
2019-07-13 13:54:59.115 - Signal id 1127, (Jog Enabled), changed from LOW to HIGH.
2019-07-13 13:54:59.115 - -----ESS: Motor 2 Still
2019-07-13 13:55:07.277 - API: mcCntlGcodeExecute() called. (G91 G31 Z -5.25F5)
2019-07-13 13:55:07.477 - Attempt transition from "Idle" on event "MDI Start" Controller.cpp:1811
2019-07-13 13:55:07.477 - Signal id 1127, (Jog Enabled), changed from HIGH to LOW.
2019-07-13 13:55:07.477 - S_IDLE_on_exit
2019-07-13 13:55:07.477 - ACTION_start_mdi
2019-07-13 13:55:07.477 - S_MDI_RUNNING_on_entry
2019-07-13 13:55:07.477 - S_MDI_RUNNING2_on_entry
2019-07-13 13:55:07.478 - Signal id 1114, (Gcode Running), changed from LOW to HIGH.
2019-07-13 13:55:07.493 - Attempt transition from "MDI Running" on event "Probe" RunCanon.cpp:497
2019-07-13 13:55:07.494 - S_MDI_RUNNING2_on_exit
2019-07-13 13:55:07.494 - Signal id 1114, (Gcode Running), changed from HIGH to LOW.
2019-07-13 13:55:07.494 - ACTION_start_probe
2019-07-13 13:55:07.494 - >>>>> ESS Probe 0, Starting.
2019-07-13 13:55:07.496 - S_MDI_PROBING_on_entry
2019-07-13 13:55:07.496 - Probing: Waiting on exit event... RunCanon.cpp:236
2019-07-13 13:55:07.496 - Controller::RunCanonBuffer called AddStopReportRequest() RunCanon.cpp:76
2019-07-13 13:55:07.496 - Requesting a stopped report for axis 0 motors.
2019-07-13 13:55:07.496 - Requesting a stopped report for motor 0.
2019-07-13 13:55:07.496 - Requesting a stopped report for axis 1 motors.
2019-07-13 13:55:07.496 - Requesting a stopped report for motor 1.
2019-07-13 13:55:07.497 - Requesting a stopped report for motor 3.
2019-07-13 13:55:07.497 - Requesting a stopped report for axis 2 motors.
2019-07-13 13:55:07.497 - Requesting a stopped report for motor 2.
2019-07-13 13:55:07.497 - Waiting on SetStill...
2019-07-13 13:55:07.516 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 0
2019-07-13 13:55:07.516 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 1
2019-07-13 13:55:07.516 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 2
2019-07-13 13:55:07.516 - -----ESS: Mach requested MSG_REPORT_MOTOR_STOP Motor 3
2019-07-13 13:55:07.516 - >>>>ESS: Switching from NORMAL to PROBE state for Probe 0
2019-07-13 13:55:08.065 - -----ESS: Checking for Probe0 Strike, none yet...
2019-07-13 13:55:08.615 - -----ESS: Checking for Probe0 Strike, none yet...
2019-07-13 13:55:08.668 - Signal id 161, (PROBE), changed from LOW to HIGH.
2019-07-13 13:55:08.668 - API: mcMotionSetProbePos() called. motor 0 position 0.0000
2019-07-13 13:55:08.669 - API: mcMotionSetProbePos() called. motor 1 position 0.0000
2019-07-13 13:55:08.669 - API: mcMotionSetProbePos() called. motor 2 position 3199.0000
2019-07-13 13:55:08.669 - API: mcMotionSetProbePos() called. motor 3 position 0.0000
2019-07-13 13:55:08.669 - API: mcMotionSetProbePos() called. motor 4 position 0.0000
2019-07-13 13:55:08.669 - API: mcMotionSetProbePos() called. motor 5 position 0.0000
2019-07-13 13:55:08.669 - ^^^^^^ ESS: Success! Probe0 Strike. Switching from PROBING to PROBING_CLEANUP state.
2019-07-13 13:55:08.669 - -----ESS: Mach ACKs Probe0 input signal ON!
2019-07-13 13:55:08.718 - ^^^^^^ ESS Probe0 Finished: The device is still and the buffer is empty.
2019-07-13 13:55:08.718 - API: mcMotionClearPlanner() called.
2019-07-13 13:55:08.718 - API: mcMotionSetProbeComplete() called.
2019-07-13 13:55:08.718 - Recording latched probe positions.
2019-07-13 13:55:08.718 - Attempt transition from "Probing" on event "Probe Complete" MachAPI.cpp:1348
2019-07-13 13:55:08.718 - S_MDI_PROBING_on_exit
2019-07-13 13:55:08.719 - ACTION_stop_probe
2019-07-13 13:55:08.719 - >>>>> ESS Probe 0, Done
2019-07-13 13:55:08.721 - S_MDI_RUNNING2_on_entry
2019-07-13 13:55:08.721 - Signal id 1114, (Gcode Running), changed from LOW to HIGH.
2019-07-13 13:55:08.723 - SyncPosition()! Clearing planner.
2019-07-13 13:55:08.723 - .^^^^^ESS: Switching from PROBING_CLEANUP to NORMAL state.
2019-07-13 13:55:08.723 - Waiting on SetStill is Done!
2019-07-13 13:55:08.723 - Probing: Exiting hold because of probe strike. GcodeExec.cpp:1272
2019-07-13 13:55:08.793 - Signal id 161, (PROBE), changed from HIGH to LOW.
2019-07-13 13:55:08.794 - -----ESS: Mach ACKs Probe0 input signal OFF.
2019-07-13 13:55:08.843 - Attempt transition from "MDI Running" on event "Stop" GcodeExec.cpp:1099
2019-07-13 13:55:08.843 - S_MDI_RUNNING2_on_exit
2019-07-13 13:55:08.843 - Signal id 1114, (Gcode Running), changed from HIGH to LOW.
2019-07-13 13:55:08.843 - S_MDI_RUNNING_on_exit
2019-07-13 13:55:08.843 - ACTION_stop
2019-07-13 13:55:08.869 - S_IDLE_on_entry
2019-07-13 13:55:08.870 - API: mcCntlGcodeExecute() called. (G 91
F 5)
2019-07-13 13:55:09.070 - Attempt transition from "Idle" on event "MDI Start" Controller.cpp:1811
2019-07-13 13:55:09.070 - S_IDLE_on_exit
2019-07-13 13:55:09.070 - ACTION_start_mdi
2019-07-13 13:55:09.070 - S_MDI_RUNNING_on_entry
2019-07-13 13:55:09.070 - S_MDI_RUNNING2_on_entry
2019-07-13 13:55:09.071 - Signal id 1114, (Gcode Running), changed from LOW to HIGH.
2019-07-13 13:55:09.093 - API: mcCntlEStop() called.
2019-07-13 13:55:09.093 - API: mcCntlEnable(false) called.
2019-07-13 13:55:09.093 - API: mcCntlCycleStop() called.
2019-07-13 13:55:09.093 - Signal id 1019, (Enable #1), changed from HIGH to LOW.
2019-07-13 13:55:09.094 - Signal id 1021, (Enable #3), changed from HIGH to LOW.
2019-07-13 13:55:09.094 - Signal id 1020, (Enable #2), changed from HIGH to LOW.
2019-07-13 13:55:09.094 - Attempt transition from "MDI Running" on event "Stop" Controller.cpp:4535
2019-07-13 13:55:09.094 - S_MDI_RUNNING2_on_exit
2019-07-13 13:55:09.094 - Signal id 1114, (Gcode Running), changed from HIGH to LOW.
2019-07-13 13:55:09.094 - S_MDI_RUNNING_on_exit
2019-07-13 13:55:09.094 - ACTION_stop
2019-07-13 13:55:09.095 -
2019-07-13 13:55:09.095 -    $$$ ESS: Mach4 had a Cycle Stop - Force Output Stop Sates Now
2019-07-13 13:55:09.095 - Attempt transition from "MDI Running" on event "Stop" MachAPI.cpp:2678
2019-07-13 13:55:09.095 -    !!! ESS: Stop Event IGNORING command to turn OFF DISABLED output Port1-Pin14 - Spindle ON Relay
2019-07-13 13:55:09.095 -    $$$ ESS: Finished processing the Stop Event
2019-07-13 13:55:09.096 -
2019-07-13 13:55:09.120 - S_IDLE_on_entry
2019-07-13 13:55:09.120 - Signal id 1120, (Machine Enabled), changed from HIGH to LOW.
« Reply #27 on: July 13, 2019, 01:26:37 PM »
so what actually happened? I presume from reading the log that you MDI'ed a g31 z-5.25 f5?
It appeared in the log file that the probe move occurred, a probe event was detected, the motors were set to still,
the position was latched, the remainder of the move was cleared......all looks normal.
What did the machine do?
« Reply #28 on: July 13, 2019, 06:24:39 PM »
I set the "Retract Distance" to 5mm
I set the "Touch Plate Height to 4.76mm
What I wanted to happen:  Probe to the top of the touch plate, stop, retract 5mm and set the z axis to 9.76mm (5+4.76)
What actually happened:  Proved to the top of the touch plate and stopped.   Did not retract and did not set the Z height.
When I looked at the tutorial video on touch probing, it shows the exact behavior I am trying to get.   If this is not a standard behavior, then why show it in the tut and why collect the retract distance and the touch plate height.
Charlie
« Reply #29 on: July 13, 2019, 11:49:08 PM »
the log file you posted never got as far as a retract move.
Code: [Select]
This occurred at the end of what appeared to be a successful g31 probe move. The g31 executed, the probe event was detected
and yet at 13:50:32.848 Mach4 was disabled, and apparently by the ESS if I read the log file correctly. Its not easy to
interpret a log file but I'm sure smurph or Chaoticone or Daz or......will assist.
The reason the machine never retracts is because Mach is disabled BEFORE the retract is enacted.
Solve the problem of the 'probe clean-up phase' so Mach is not disabled and the bet is everything will work OK thereafter.
