Chances are you won't need the full 1.5kw VFD output (approx 6 amps@400hz,3ph,230v) unless you are taking heavy cuts with a large cutter and high feed rates so the motor kw or HP difference between 1.5kw and 2.2kw is a moot point. The worst thing that will happen is stalling the motor. You can watch the motor amps on the VFD display. Also be aware the all cheap Chinese VFD's operates in V/F (volts to frequency) mode which means as the output frequency is reduced, i.e speed control, the output voltage is reduced which affects motor torque. High quality industrial VFD's such as Toshiba and Siemens can run in vector mode to eliminate this problem.