Shielding is very important and the best practice is to shield everything. I also try to keep all signal wires away from power wires when I layout a panel. AC one side, DC the other, that kind of thing.
Something to understand about grounding. By the National Electric Code ground loops, grounding everything to everything is a good thing. That is because the intent of power grounding is to make sure that when something faults and hundreds or thousands of amps are flowing through the grounding system, no two points you could touch will ever have a voltage difference large enough to hurt you. All electrical equipment leaks power to ground, some very small amounts some very large. So power grounding systems will ALWAYS have current flowing through them. I have to laugh when electronic engineers tell you that you need to have the mythical 'clean' ground!
Control grounding is very different, as what we care about is not having a signal created, distorted, or destroyed by noise. In control grounding of devices and cable shielding you want to make sure first that there is only one ground point that connects the control grounding to the electrical power ground. Then you must make sure that every device ground and every cable shield connects to that ground point by just one path. This sounds simple, however what usually trips people up is that manufacturers of devices like pressure transmitters will provide a ground terminal, and internally they connected it to the metal case. So if you connect your cable shield to that terminal and to the ground point at the other end you now have two paths, one through the cabinet, one through the cable shield, which is bad. Another touchy spot is shielded cables passing through a junction box. It is tempting to tie the in and out shields to a ground bar that the box may have. However in junction boxes shield wires must be insulated the same as conductors. Otherwise you create multiple ground paths.
That's it, hope that helps.