Hi all

is there anyone out there using a GS2 drive over modbus on the pc serial port? if so, could you let me know how to configure the connection.

i can connect to a dl06 and read the inputs and turn on the output and coils, so i know the connection works. it is probably only some parameters to fix.
Re: GS2 drive and modbus
« Reply #1 on: April 01, 2009, 08:32:14 PM »


You will have to use a rs232 to rs485 converter to set up with mach or drive software the converter from automation direct is called an FAISOCON last I new they were about $100or so
and make your own cables with RJ45 connector don't mistake that 4 Ethernet very bad 4 PC'S modbus uses 15+volts ,But that means you can power the converter from the modbus port on the drive


Adam
Adam
Re: GS2 drive and modbus
« Reply #2 on: April 02, 2009, 06:28:12 AM »
UPDATE

Sorry about the bad info on the drive the modbus port is a RJ22 plug not RJ45 but you will still need the 232 to 485 conveter to talk to mach
Adam
Re: GS2 drive and modbus
« Reply #3 on: April 02, 2009, 08:47:29 AM »
unlike the GS1, the GS2 has a dip switch to toggle between RS232 and RS485 communication, are you sure i need an additional converter?
Re: GS2 drive and modbus
« Reply #4 on: April 03, 2009, 06:18:47 PM »
If you can toggle between 232 and 485 yes there is no need for a converter