Mach4 General Discussion / Re: SSR m7 serial
« on: April 13, 2021, 02:03:10 PM »
You can also use a Pokeys to control that SSR. And that will also give you lots of expansion. Pokeys operates on 3.3v so you have to use SSRs to switch higher voltages. As for inputs, you need to use logic level voltage switches (like PNP or NPN prox switches) as well. No mechanical switches on 3.3v inputs, as they will be noisy.
I really wouldn't use anything that is serial if you can help it. Ethernet is way better in the long run.
An example of a low cost PLC, Ethernet, 8 DC inputs and 6 relay outputs. No SSR needed with the relays on the outputs. It does require a 24v power source:
https://www.automationdirect.com/adc/shopping/catalog/programmable_controllers/click_series_plcs/click_plcs_(stackable_micro_brick)/plc_units/c0-10dre-d
The PLC isn't $12.00 like that serial modbus thing, but it is a more industrial solution.
Steve
I really wouldn't use anything that is serial if you can help it. Ethernet is way better in the long run.
An example of a low cost PLC, Ethernet, 8 DC inputs and 6 relay outputs. No SSR needed with the relays on the outputs. It does require a 24v power source:
https://www.automationdirect.com/adc/shopping/catalog/programmable_controllers/click_series_plcs/click_plcs_(stackable_micro_brick)/plc_units/c0-10dre-d
The PLC isn't $12.00 like that serial modbus thing, but it is a more industrial solution.
Steve