I will have a read through the information you have provided, yes I have the manual for mine rated voltage is 100 Volts in the user guide.
The input is 4.7KVA at rated output of 40 Amps, so really wants a 22Amp supply but duty cycle is 60% at that those figures.
I need to run the machine under 25 Amps if I can reasoning is it is on a 13 amp socket.
220 Volts x 13Amps = 2860 KVA * 0.85% efficiency I have 2431 KVA available, 100 Volts rated so around 24 amps cutting current.
I can push a bit higher but the garage supply which is really only rated at 20 Amps has to power PC, lights and a compressor.
Thanks for the rest of the information I will read through the posts you have listed, thanks for that.
UK is 230v
100v(OP) x 40A(OP) = 4kW (OP)
4kW / 0.85 (%eff) = 4.7kW [so that checks out]
4.7kW / 230v = 20.4A
You can probably get away with a 16A BS60309 plug and socket [I do with my powermax 45 (45A @ 132V, 0.99 power factor = 5,940kW), 6kVA at 25A generator recommended]
http://www.toolstation.com/shop/Electrical/d190/Industrial+Connectors/sd2430/Industrial+Plug+IP44/p36175http://www.toolstation.com/shop/Electrical/d190/Industrial+Connectors/sd2430/Industrial+Socket+IP44/p20698advantage is that they aren't fused .... so have a bit more give than a 13A plugtop.
looking at another 3A per 1hp for the compressor (approx),
duty cycle is the operating time per 10 min duty cycle (hence 60% duty cycle means 6 mins run time, 4 mins cooloff).
on a 20A mcb, you can probably get away with around 30A maybe a little more at that duty cycle depending upon breaker or fuse type..... also you'll find that your actual cut time probably won't be 6 mins anyway (as that would be ~ 5m of cutting at your feedrate.... continious on a small table..... not really possible in my opinion
http://wiki.diyfaq.org.uk/images/d/d4/Curve-MCBTypeB.pnghttp://wiki.diyfaq.org.uk/images/thumb/d/d6/Curve-MCBTypeC.png/640px-Curve-MCBTypeC.pngI was told by a hypertherm technical person that as a guide (starting point) if you've got the feedrates for 40A, and reduce the ampage to say 32A (20% reduction), then your feedrate should drop by a corresponding percentage (roughly).