456
« on: November 07, 2014, 06:42:43 PM »
One thing for sure, if an earth ground appears to fix your problem you haven't found the problem! I always consider this solution to be hocus pocus and possibly hiding a problem that could get you killed. A large part of the problem is that electronic engineers don't seem to understand that electronic signal grounding and power grounding are completely different. So they go looking for the mythical 'clean ground', which is what that earth ground is supposed to supply. Nothing could be further from the truth.
In power grounding the purpose is to ensure that no two adjacent grounded points ever have a voltage difference that can kill. Everything electrical leaks power to ground, all the time. When things go bad, like a motor winding going to ground that 'leakage' may be thousands of amperes! So by connecting everything together creating as many 'ground loops' as you possibly can you ensure that a very small voltage difference is all you see from that railing you have in one hand the handle you have in the other.
In electronic signal grounding you simply want no current flowing on the shielding because when done properly one one end is ever connected to ground. Hence only the very small currents from signal leakage and induced currents through the air will ever flow through that shield. In order not to have ground loops you MUST check whether devices have ground connections to their cases. The single grounding point works only if no other device ties to ground through the frame of the machine. If the ground point of the device is already grounded to the frame, insulate the shield from ground at that point, and make sure it is connected to the common ground point only back in the panel.
One reason your problem may happen when you turn the power off not on is because that is when the magnetic field in the contactor coil collapses and created a large back EMF. You should have a suppressor on the coil in any event. In the early days of digital meters I fried a few on contactor coils when I hit the stop button!
Opening the contactor to the VFD has a similar effect, an arc is drawn for an instant, and there is a large surge. I suspect the monitor is not going off on low voltage because it happens when you turn other devices off. So that suggests it is going off due to seeing a high voltage when arcing or a load dump occurs. I'd check your VGA cable to if it connects the shield to ground at both ends, because that is likely to be the case.
Hope you get your problem sorted quickly.