General Mach Discussion / Re: My spindle keeps shutting off randomly.
« on: February 09, 2015, 02:41:16 PM »
Ok... finally getting somewhere!
My machine is a IHCNC turnkey (using their term loosely)
I called Factory Automation. .. great people by the way! My VFD was hooked up to L1 and L2 from factory.... L1 and L3 is what it is supposed to be.
It seems to work! But.... it uses a 20 amp breaker for control cabinet on off switch. At full RPM no load that breaker will trip after 10 minutes of running. Breaker is getting warm... not hot... should I just replace breaker... or do I have bigger problems?