« on: July 18, 2013, 09:07:52 PM »
Putting a voltmeter on the VFD will tell you nothing of value. You need to be looking at current, which means putting an ammeter *in series* with one phase of the motor. The Tormach load meter is nothing but an analog ammeter. An analog ammeter contains a shunt, which is a very small, precisely known resistance. When current passes through it, it creates a small voltage drop (typically 50mV at maximum allowed current), and the meter itself is a very sensitive voltmeter, connected across the shunt, that reads full-scale with 50mV across it. Look at digikey, mouser, and other electroincs supply houses, and find one with a suitable full-scale reading. But, a good analog ammeter will not be cheap. However, a digital meter, in this application, would be completely useless.
Regards,
Ray L.