To add a little more to the BSMCEO4U-PP definitions.
1) 24V: Input can be anywhere from 12V to 36V to power the digital input and outputs only. It is usually the same voltage that supplies the motor drivers, but it can be a separate supply (200ma minimum).
2) DCM: connection is digital ground for both input switches (Limits, E-Stop, & Probe) and output loads (VFD Start, Flood, & Mist).
3) ACM is the analog ground specifically for the spindle speed control. It goes to the ACM pin on the VFD.
4) AVI: is the analog output to the spindle speed control. (not very linear). It goes to the AVI pin on the VFD.
5) 10V: is the input analog reference voltage for the spindle speed control. This should come from the VFD low voltage supply (10V to 13V) output.
6) 5V: is a low power output to supply the motor driver opto-isolators providing you use "Low-True" logic (pull to ground for ON)
7) GND: output is the ground to the motor drivers used when driving "High-True" logic (Pull to 3,3V to 5V for ON).
Note: For the motor drivers, you will use either the 5V or the GND connection, not both. Choosing the right method may require some experimentation.
Note: DCM, ACM, and GND (all grounds) are not connected together. Each serves an isolated purpose, and their isolation is an attempt to protect your equipment. If you want everything grounded together (and you should), run a separate ground wire from each piece of equipment to a common grounding point near your master power input. This method should prevent a single failure from destroying everything.
Thanks.
Bill