« on: May 06, 2013, 03:03:23 PM »
Hey Troy, I just spoke to AUD and they say the GS2 can not work like that. The problem I'm having with the source of operation for the Fwd/Rev, Stop/Run being respected if the parameter is changed by serial. The drive does a great job and I like it. This would have been no problem had I known up front. I called AUD a couple of months ago when I was thinking about this option and they said it would work fine........ now they say it won't. Soooooo, I will probably be redoing the controls a bit. I'm thinking right now that I will have the digital inputs run through a set of dry contact relays and simply have mach or my front panel selector switch turn them on or off. In hind sight, I would have put a PLC in my VFD/manual spindle control box and handled all IO and serial communications through it. I have sent you a PM as well Troy.
The only way I see around this caveat is if you could enable/disable a config. in the serial plug-in modbus via vb.
Brett