General Mach Discussion / Re: Mach 3 outputs 15hz to vfd instead of 0
« on: July 13, 2019, 04:32:19 AM »
Thank you for your time to weite such a informative post. I will take a look into those.
This section allows you to view all posts made by this member. Note that you can only see posts made in areas you currently have access to.
Hi,
while its not perfect it is about what I would expect.
PWM is quite hard to achieve if you must also have perfect 0% modulation simultaneously with perfect 100% and linearity.
If your demands are that stringent then you should consider a step/direction servo and matching servo drive as a spindle.
Craig
Hi,
the most likely explanation is that Mach3 or your BoB doesn't quite go all the way to 0V.
With a multimeter measure the 0-10V signal and confirm the range it actually achieves, especially the bottom end.
Note that is not correct to stop the spindle in Mach just by specifying zero speed (S0.00). You should use M5 because
this opens the ON/OFF relay. If you rely on S0.00 any noise or linearity fault could cause the spindle to turn unexpectedly
because the relay is still ON. This could have injurious consequences if you were doing a manual tool change.
Craig