Third party software and hardware support forums. => Modbus => Topic started by: ulihuber on September 23, 2017, 01:06:32 PM
-
Hi all,
I have connected my Danfoss VFD (FC302) to Mach3 by Modbus TCP.
Now I want to extend I/Os with another Modbus TCP device. But I have only one IP address I can configure in the Mach3 Modbus TCP plugin.
Is this really this step backwards from serial Modbus RTU, wher I can configure several Modbus addresses ??
Or have I missed something?
Thanks
Uli
-
OK, as no one offered a solution, I did my own thing - the 'TCP Modbus Broker'... >:D
I found out that the Modbus-TCP-packet still contains the slave address which can be entered in each row of the Modbus plugin.
So I wrote a piece of software which presents itself to Mach3 as a single Modbus-TCP Client and uses the slave address to divert the Modbus telegrams to different IP adresses (or DNS-names)
For portability reasons it is done in Python (ver 3.3.).
It has to be started before Mach3 manually or in a batch unsing the command line
mmb.py [-test] [-quiet] Client-Address_1 ...[Client-Address_n]
-quit Makes the program just count packets as indication of proper operation. If it is omitted, full data of all packages is displayed
-test Allows local testing with TCP echo-clients by diverting to two adresses and using port 503 and 504 instead of modbus port 502. Not for production usage!
In Mach3 Modbus-TCP-plugin you enter 127.0.0.1 as IP-address if the program runs on the same computer. If you decide to run it on an other computer (i.e. Raspberry or cheap Orange-Pi), use the appropriate address of the device.
Have fun!
Uli
#UHU Modbus TCP Message Broker
#
# Ermöglicht die Nutzung mehrerer Modbus-TCP-Devices an Mach3, das im Modbus-TCP-Plugin zwar Slave-
# Adressen zur Eingabe anbietet, aber leider nur eine IP-Adresse verwalten kann.
#
# Das Programm stellt sich gegenüber Mach3 als Modbus-TCP-Device dar und verteilt Modbus-Anfragen
# auf die angegebenen im Netz befindlichen Clients (Netzwerkadressen oder DNS-Namen)
# Dabei entspricht der erste angegebene Client dem Slave #1 aus der Mach3 Modbus TCP Konfiguration.
#
# Voraussetzung: Installierter Python Interpreter >Ver3.0 (frei im Web verfuegbar)
#
# Aufruf mit mmb.py [-test] [-quiet] Client-Adresse_1 [Client-Aderess_n]
#
# -quiet Statt der Ausgabe der vollständigen Daten der Modbus-Telegramme wird nur ein Zähler
# dargestellt, an dem man erkennen kann ob Pakete einwandfrei transportiert werden.
#
# -test baut eine Verbindung zu zwei angebbaren Clients unter den Portadressen 503 und 504 auf.
# Dies ist nützlich, wen man für Tests statt echter Hardware lokale, virtuelle Modbus-TCP Clients
# mit dem Tool TCP-Responder.py nutzen möchte
#
# Eingebaute Features:
# Reconnect bei Ausfall eines (oder aller) Clients
# Reconnect bei Neustart von Mach3. Leider baut Mach3 eine abgebrochene Verbindung zu einem Modbus-TCP-Client
# nicht von selbst wieder auf, auch nicht durch RESET. Dies kann ein Problem geben, wenn der Modbus-Broker
# auf einem anderen Rechner läuft und dieser z.B. neu startet. Dann muss man Mach3 neu starten oder in
# den Einstellungen für das TCP-Modbus-Plugin 'APPLY' drücken.
#
#
import socket
import sys
import struct
PORT = 502
def printInline(t):
global pkgCtr
if quiet:
pkgCtr +=1
t = str(pkgCtr)
delete = "\b" * len(t)
print("{0}{1}".format(delete, t), end="")
sys.stdout.flush()
else:
print(t)
def connHost(sockH):
print ("Waiting for Modbus Host on port " + str(PORT))
connection, NetAddr = sockH.accept()
print( 'Connected by '+str(NetAddr))
print()
return connection
def connSlave(NetAddr,i):
if not testClients:
port = PORT
else:
if i == 1:
port = 503
else:
port = 504
print ("\nConnecting slave " + str(i) + " to " + NetAddr + " on port " + str(port))
sock = socket.socket(socket.AF_INET, socket.SOCK_STREAM)
connected = False
while not connected:
try:
sock.connect((NetAddr, port))
sock.settimeout(2)
print ("Slave " +str(i) + " connected to " + NetAddr)
connected = True
except Exception:
pass
return sock
def connectSlaves(Slaves):
for s in Slaves:
SlaveArray = Slaves[s]
i = SlaveArray[0]
SlaveArray[1] = connSlave(s,i)
Slaves[s] = SlaveArray
print("\n------------------------------------------")
return Slaves
def closeSlaves(Slaves):
print()
for s in Slaves:
SlaveArray = Slaves[s]
print ("Closing slave " + str(SlaveArray[0]) + " : " + s)
SlaveArray[1].close()
def relay(Slaves):
HOST = ''
sockH = socket.socket(socket.AF_INET, socket.SOCK_STREAM)
sockH.bind((HOST, PORT))
sockH.listen(1)
Host = connHost(sockH)
Slaves = connectSlaves(Slaves)
print ("Connected to Modbus devices")
while 1:
try:
dataOut = Host.recv(1024)
except socket.timeout:
print ('Timeout')
Host.close()
Host = connHost(sockH)
break
except Exception as e:
print("Exception")
print(e)
break
if not dataOut: break
printInline('%15s %30s' %('Host: ',repr(dataOut)))
modSlave = dataOut[6]
for s in Slaves:
SlaveArray = Slaves[s]
i = SlaveArray[0]
if str(modSlave) == str(SlaveArray[0]):
try:
SlaveArray[1].send(dataOut)
except Exception:
closeSlaves(Slaves)
Slaves = connectSlaves(Slaves)
try:
dataIn= SlaveArray[1].recv(1024)
printInline('%15s %30s' %(s +': ',repr(dataIn)))
if len(dataIn) < 100:
Host.send(dataIn)
except Exception:
closeSlaves(Slaves)
Slaves = connectSlaves(Slaves)
Host.close()
closeSlaves(Slaves)
def _main():
global pkgCtr
global testClients
global quiet
Slaves = {}
testClients = False
quiet = False
pkgCtr = 1
if len(sys.argv)== 1:
print("\n\nAufruf: mmb.y [-test] [-quiet] Net-Address1 [Net-Address2] ... [NetAddress(n)]\n\n")
while 1: pass
else:
CntSlaves = 0
for i in range(1, len(sys.argv)):
if sys.argv[i] == "-test":
testClients = True
print("Option: Test")
if sys.argv[i] == "-quiet":
quiet = True
print("Option: Quiet")
if not sys.argv[i][0] == "-":
CntSlaves += 1
NetAddr = sys.argv[i]
SlaveArray = [CntSlaves,"x"]
Slaves[NetAddr] = SlaveArray
relay(Slaves)
if __name__=='__main__':
_main()
-
hello ,
can I ethernet connect Mach3 MODBUS TCP - PC to STM32 via modem router or
is it possible only with crossover cable ?
thank you
( STM32 is the microcontroller at my own board )
-
you can always connect two ethernet interfaces with crossover - provided that you set matching ip adresses manually.
Uli
-
hello thanks for answering
but I am afraid I couldot express myself clearly
I am trying to MODBUS TCP IP comunicate the Mach3 with my own made ethernet plc
this here:
http://www.oem-plc.com/index15.htm
however I am stuck at the step of TCP IP connection process
whatever I do Mach3 gives "connetion tinmeout" error
my Mach3 PC and the PLC are connected to each other via router modem
now I want ask how did you connect Mach3 with PLC ?
is there a modem or switch inbetween
or did you conected your Mach3 to the PLC with crossover cable ?
I am wondering it is posible with modem router or shall I use crossover cable absolutely
thank you
-
Hi,
I am sorry but this has got nothing to do with my posted software here. It is an issue with your PLC.
You have to ask the manufacturer of the PLC for specifics, he should be able to help you.
Uli
-
dear friend ,
please , I am asking a simple question
did you connected your PLC to Mach3-PC via ethernet switch or router modem or something like that ?
or did you connected PLC and Mach3-PC direct to each other with ethernet cable ( without anything inbetween ) ?
thank you
-
Listen, the simple question was answered in my first (simple) answer.
There is no difference between cross-cable and switch connection- if addresses are set correctly. Both will work identically. I used a cross cable.
And I can't say anything about your PLC. I don't know it and I do not have the time to work into it. Sorry.
Uli