I'm wiring my four stepper motors 18AWG shielded cables and I want to know how I ground physically the cable shields at the panel end.
When I cut the exterior plastic shell of each cable, there is under it the metal braiding and after there is the aluminum foil; do I ground only the braiding, the foil, both?
And how do you do this physically? Do I solder a piece of wire to the braiding / foil ?
Thanks
-
Solder a short piece of stranded wire to the copper braid only. The foil can be trimmed out of the way.
John Champlain
-
Thank you John
Was planning doing so but thought maybe there is a better way
-
^ That's how I've always done it on every sort of equipment I've worked on. For tidiness, pop a bit of self-adhesive heat shrink over the transition between the braid and the insulated wire tail ;)
-
Good point, makes for a better looking connection
-
I've used the heat shrink solder type butt splices for this. Just put the two ends into the splice and heat with a heat gun. Solder melts and tube shrinks at the same time. It looks very neat.
-
Don't know about this Gary but I will try to find out. Sounds a good idea
-
Forgot to mention, Home Depot has them
-
Thanks for the tip.
Just found them on HD site but they only have for 14, 12 and 10AWG. Will try elswhere because I need for 18AWG