Have a strange problem. For some reason I can't read a PLC output using a Brain. Can write to a PLC with a Brain, but can't read. It reads fine using the Modbus test window in Mach3, but not from within a Brain. Any idea what could be the reason? Attached screenshots of the Modbus settings and the Brain.
Thanks,
Dan
-
you need to use the serial modbus brain inputs,
see "Brains Users Guide" under member docs.
Scott
-
Hi Scott,
I am using that document and it's very helpful! Thank you for writing it.
Not sure what you mean, though. Please see screenshot showing how I am doing the input for the Brain shown above.
Dan
-
Strange thing is that I am able to read outputs from the VFD using same Brain. Then why it wouldn't read from the PLC? Again, what's most strange is that I can read the PLC inputs using the Test window in Mach3. Only doesn't work fro a Brain.
Dan
-
Problem solved. Was wrong communication settings in the PLC.
Thanks,
Dan
-
I looked for Brains User Doc under documentation but I could not find it. I saw the videos but I would like to look at text. Could some one point me in the right direction. I would like to connect to my VFD using the PLC capabilities of my VFD and I want to read how to do it.
Thanks
-
You can download it from here:
http://www.machsupport.com/forum/index.php/topic,8211.0.html
-
Dan,
Thank you. After searching my computer, I discovered that I had a copy. But I am sure others will find the link usefull. Now to make it work.
Regards,