Mach Discussion => General Mach Discussion => Topic started by: tantrim on July 17, 2009, 01:57:41 PM
-
I am running a Gecko 540. I ran a wire to Input #4 and another to -V then clicked on Config-Ports and Pins-Input Signals. There I enabled Probe, changed pin# to 13, Changed active low to green check. At this point I am manually touching the wires together after clicking on the Z button in the Automatic Tool Probing screen. As Z axis moves downward I touch the wire together and it makes a rapid movement down an additional 1/2" or so before moving up. What do I need to do to correct the move down after the wires have been touched together?
-
Hi, Tantrim
Look at this Post, It's probably what's going on with your setup.
http://www.machsupport.com/forum/index.php/topic,5673.0.html
Try typing a G49 on the MDI line and Enter key, Then try it again, See if that Helps.
Chip
-
I rebooted the computer and it has corrected it self. It seems to work now. I will look into the site.
Thanks