Mach Discussion => General Mach Discussion => Topic started by: amontgom on March 08, 2011, 12:28:19 AM
-
i am converting an older Anilam Eagle cnc km-750..
during the course i have gotten most everything working once again with a new drive package..
i am using LeadShine M860 stepper driver in 1600 microstepping mode and Leadshine 4.5 NM NEMA34 motors ( 1/2" shafts) in parallel coil configuration and a cnc4pc c-10 breakout board ( one more on order for i/o) the axis tests are perfect ( almost better than original.. .0002 resolution) .. someone had the brains to have a ball screw cover..
the problem..
the spindle once had a vfd and had an air controlled variable spindle speed setup...
i am converting the air system with a stepper .. and the vfd is toast.. i have spent so much money in fancy controls and doo dads.. i am holding off on a replacement vfd for a few months.
i am replacing it with a set of 3phase contactors.. one for cw the other for ccw and one for e-stop that kills power to the whole motor circuit. ( for redundant protection)
the problem i am wondering is when i issue a m3 or m4 command is there an xor designed into the software to prevent the simultaneous output on both the pins assigned to m3 and m4?
or should i design a safety circuit that xor's the output and ands them back into the relays controlling the 3phase contactors?
another question is the output of the signal of the m3/4 is it a pulse or is it a sustained signal high or low until i issue a m0 or e-stop.
way too many questions .. but i have not seen the topics asked or answered yet..
(http://)
-
The M3 and M4 will toggle one or the other and when assigned different outputs will not both be on at the same time.
The output signal from the M3 / M4 command is a steady state high or low.
I never leave anything to chance with 3 phase so, if it is possible, it would not hurt to incorporate an interlock into your contactors just to be sure to be sure ;)
Tweakie.
-
thanks.. i thought it would be that case.. but wanted to be sure.. i will still build the xor safety circuit just to be certain that it is not possible to cross phases during a crash or catastrophic software failure..
-
The software should only activate one or the other but personally I would not rely totally on software. Depending on your contactor type you may be able to get a mechanical link between them which will prevent one being operated if the other is already operated, my lathes contactors were like that.
Regards output, it is a steady signal and also M5 will also stop it.
Hood
-
ah too slow in typing I see ;D
-
exactly..
i want to idiot proof the design.. JIK someone else decides to bypass the contactor interlocks.. ( stranger things have happened) ..
how is Scotland tonight?
-
Afraid I dont know how Scotland is tonight as its only morning ;D
Safety is always a good thing, especially when talking mains voltages.
Hood