 Modbus over serial line - RTU Slave Arduino Sketch 
void configure_mb_slave(long baud, char parity, char txenpin);
int update_mb_slave(unsigned char slave, int *regs,
unsigned int regs_size);
int t1,t2,t3,t4,t5 ;
/* Modbus RTU common parameters, the Master MUST use the same parameters */
enum {
        MB_SLAVE = 1,	/* modbus slave id */
/* slave registers example */
enum {        
        MB_REG0,
        MB_REG1,
        // line below is for holding registers.    'vinny'
        MB_REGS	= 40 	/* total number of registers on slave */
int regs[MB_REGS];	/* this is the slave's modbus data map */
void setup() 
        /* Modbus setup example, the master must use the same COM parameters */
        /* 115200 bps, 8N1, two-device network */
        //  changed to 19200  bps, 8N1, two-device network 'vinny'
        configure_mb_slave(9600, 'n', 1);
        pinMode(2, INPUT_PULLUP);
  pinMode(3, INPUT_PULLUP);
  pinMode(4, INPUT_PULLUP);
  pinMode(5, INPUT_PULLUP);
  pinMode(6, INPUT_PULLUP);
  pinMode(7, INPUT_PULLUP);
  pinMode(8, INPUT_PULLUP);
  pinMode(9, INPUT_PULLUP);
void loop() 
        /* This is all for the Modbus slave */
	update_mb_slave(MB_SLAVE, regs, MB_REGS) ;
regs[0]=analogRead(A0);
regs[1]=analogRead(A1);
regs[2]=!digitalRead(2);
  regs[3]=!digitalRead(3);
  regs[4]=!digitalRead(4);
  regs[5]=!digitalRead(5);
  regs[6]=!digitalRead(6);
  regs[7]=!digitalRead(7);
  regs[8]=!digitalRead(8);
  regs[9]=!digitalRead(9);
 * BEGIN MODBUS RTU SLAVE FUNCTIONS
/* global variables */
unsigned int Txenpin = 0;        /* Enable transmission pin, used on RS485 networks */
/* enum of supported modbus function codes. If you implement a new one, put its function code here ! */
enum { 
        FC_READ_REGS  = 0x03,   //Read contiguous block of holding register
        FC_WRITE_REG  = 0x06,   //Write single holding register
        FC_WRITE_REGS = 0x10    //Write block of contiguous registers
/* supported functions. If you implement a new one, put its function code into this array! */
const unsigned char fsupported[] = { FC_READ_REGS, FC_WRITE_REG, FC_WRITE_REGS };
/* constants */
enum { 
        MAX_READ_REGS = 0x7D, 
        MAX_WRITE_REGS = 0x7B, 
        MAX_MESSAGE_LENGTH = 256 
enum { 
        RESPONSE_SIZE = 6, 
        EXCEPTION_SIZE = 3, 
        CHECKSUM_SIZE = 2 
/* exceptions code */
enum { 
        NO_REPLY = -1, 
        EXC_FUNC_CODE = 1, 
        EXC_ADDR_RANGE = 2, 
        EXC_REGS_QUANT = 3, 
        EXC_EXECUTE = 4 
/* positions inside the query/response array */
enum { 
        SLAVE = 0, 
        FUNC, 
        START_H, 
        START_L, 
        REGS_H, 
        REGS_L, 
        BYTE_CNT 
CRC
 INPUTS:
 	buf   ->  Array containing message to be sent to controller.            
 	start ->  Start of loop in crc counter, usually 0.
 	cnt   ->  Amount of bytes in message being sent to controller/
 OUTPUTS:
 	temp  ->  Returns crc byte for message.
 COMMENTS:
 	This routine calculates the crc high and low byte of a message.
 	Note that this crc is only used for Modbus, not Modbus+ etc. 
unsigned int crc(unsigned char *buf, unsigned char start,
unsigned char cnt) 
        unsigned char i, j;
        unsigned temp, temp2, flag;
        temp = 0xFFFF;
        for (i = start; i < cnt; i++) {
                temp = temp ^ buf[i];
                for (j = 1; j <= 8; j++) {
                        flag = temp & 0x0001;
                        temp = temp >> 1;
                        if (flag)
                                temp = temp ^ 0xA001;
        /* Reverse byte order. */
        temp2 = temp >> 8;
        temp = (temp << 8) | temp2;
        temp &= 0xFFFF;
        return (temp);
 * 	The following functions construct the required query into
 * 	a modbus query packet.
 * Start of the packet of a read_holding_register response 
void build_read_packet(unsigned char slave, unsigned char function,
unsigned char count, unsigned char *packet) 
        packet[SLAVE] = slave;
        packet[FUNC] = function;
        packet[2] = count * 2;
 * Start of the packet of a preset_multiple_register response 
void build_write_packet(unsigned char slave, unsigned char function,
unsigned int start_addr, 
        packet[START_H] = start_addr >> 8;
        packet[START_L] = start_addr & 0x00ff;
        packet[REGS_H] = 0x00;
        packet[REGS_L] = count;
 * Start of the packet of a write_single_register response 
void build_write_single_packet(unsigned char slave, unsigned char function,
        unsigned int write_addr, unsigned int reg_val, unsigned char* packet) 
        packet[START_H] = write_addr >> 8;
        packet[START_L] = write_addr & 0x00ff;
        packet[REGS_H] = reg_val >> 8;
        packet[REGS_L] = reg_val & 0x00ff;
 * Start of the packet of an exception response 
void build_error_packet(unsigned char slave, unsigned char function,
unsigned char exception, unsigned char *packet) 
        packet[FUNC] = function + 0x80;
        packet[2] = exception;
 * modbus_query( packet, length)
 * Function to add a checksum to the end of a packet.
 * Please note that the packet array must be at least 2 fields longer than
 * string_length.
void modbus_reply(unsigned char *packet, unsigned char string_length) 
        int temp_crc;
        temp_crc = crc(packet, 0, string_length);
        packet[string_length] = temp_crc >> 8;
        string_length++;
        packet[string_length] = temp_crc & 0x00FF;
 * send_reply( query_string, query_length )
 * Function to send a reply to a modbus master.
 * Returns: total number of characters sent
int send_reply(unsigned char *query, unsigned char string_length) 
        unsigned char i;
        if (Txenpin > 1) { // set MAX485 to speak mode 
                UCSR0A=UCSR0A |(1 << TXC0);
                digitalWrite( Txenpin, HIGH);
                delay(1);
        modbus_reply(query, string_length);
        string_length += 2;
        for (i = 0; i < string_length; i++) {
                Serial.write(query[i]);
        if (Txenpin > 1) {// set MAX485 to listen mode 
                while (!(UCSR0A & (1 << TXC0)));
                digitalWrite( Txenpin, LOW);
        return i; 		/* it does not mean that the write was succesful, though */
 * 	receive_request( array_for_data )
 * Function to monitor for a request from the modbus master.
 * Returns:	Total number of characters received if OK
 * 0 if there is no request 
 * A negative error code on failure
int receive_request(unsigned char *received_string) 
        int bytes_received = 0;
        /* FIXME: does Serial.available wait 1.5T or 3.5T before exiting the loop? */
        while (Serial.available()) {
                received_string[bytes_received] = Serial.read();
                bytes_received++;
                if (bytes_received >= MAX_MESSAGE_LENGTH)
                        return NO_REPLY; 	/* port error */
        return (bytes_received);
 * 	modbus_request(slave_id, request_data_array)
 * Function to the correct request is returned and that the checksum
 * is correct.
 * Returns:	string_length if OK
 * 		0 if failed
 * 		Less than 0 for exception errors
 * 	Note: All functions used for sending or receiving data via
 * 	      modbus return these return values.
int modbus_request(unsigned char slave, unsigned char *data) 
        int response_length;
        unsigned int crc_calc = 0;
        unsigned int crc_received = 0;
        unsigned char recv_crc_hi;
        unsigned char recv_crc_lo;
        response_length = receive_request(data);
        if (response_length > 0) {
                crc_calc = crc(data, 0, response_length - 2);
                recv_crc_hi = (unsigned) data[response_length - 2];
                recv_crc_lo = (unsigned) data[response_length - 1];
                crc_received = data[response_length - 2];
                crc_received = (unsigned) crc_received << 8;
                crc_received =
                        crc_received | (unsigned) data[response_length - 1];
                /*********** check CRC of response ************/
                if (crc_calc != crc_received) {
                        return NO_REPLY;
                /* check for slave id */
                if (slave != data[SLAVE]) {
                        return NO_REPLY;
        return (response_length);
 * 	validate_request(request_data_array, request_length, available_regs)
 * Function to check that the request can be processed by the slave.
 * Returns:	0 if OK
 * 		A negative exception code on error
int validate_request(unsigned char *data, unsigned char length,
        int i, fcnt = 0;
        unsigned int regs_num = 0;
        unsigned int start_addr = 0;
        unsigned char max_regs_num;
        /* check function code */
        for (i = 0; i < sizeof(fsupported); i++) {
                if (fsupported[i] == data[FUNC]) {
                        fcnt = 1;
                        break;
        if (0 == fcnt)
                return EXC_FUNC_CODE;
        if (FC_WRITE_REG == data[FUNC]) {
                /* For function write single reg, this is the target reg.*/
                regs_num = ((int) data[START_H] << 8) + (int) data[START_L];
                if (regs_num >= regs_size)
                        return EXC_ADDR_RANGE;
                return 0;
        /* For functions read/write regs, this is the range. */
        regs_num = ((int) data[REGS_H] << 8) + (int) data[REGS_L];
        /* check quantity of registers */
        if (FC_READ_REGS == data[FUNC])
                max_regs_num = MAX_READ_REGS;
        else if (FC_WRITE_REGS == data[FUNC])
                max_regs_num = MAX_WRITE_REGS;
        if ((regs_num < 1) || (regs_num > max_regs_num))
                return EXC_REGS_QUANT;
        /* check registers range, start address is 0 */
        start_addr = ((int) data[START_H] << 8) + (int) data[START_L];
        if ((start_addr + regs_num) > regs_size)
        return 0; 		/* OK, no exception */
 * 	write_regs(first_register, data_array, registers_array)
 * 	writes into the slave's holding registers the data in query, 
 * starting at start_addr.
 * Returns:   the number of registers written
int write_regs(unsigned int start_addr, unsigned char *query, int *regs) 
        int temp;
        unsigned int i;
        for (i = 0; i < query[REGS_L]; i++) {
                /* shift reg hi_byte to temp */
                temp = (int) query[(BYTE_CNT + 1) + i * 2] << 8;
                /* OR with lo_byte           */
                temp = temp | (int) query[(BYTE_CNT + 2) + i * 2];
                regs[start_addr + i] = temp;
        return i;
 * 	preset_multiple_registers(slave_id, first_register, number_of_registers,
 * data_array, registers_array)
 * 	Write the data from an array into the holding registers of the slave. 
int preset_multiple_registers(unsigned char slave,
int *regs) 
        unsigned char function = FC_WRITE_REGS;	/* Preset Multiple Registers */
        int status = 0;
        unsigned char packet[RESPONSE_SIZE + CHECKSUM_SIZE];
        build_write_packet(slave, function, start_addr, count, packet);
        if (write_regs(start_addr, query, regs)) {
                status = send_reply(packet, RESPONSE_SIZE);
        return (status);
 * write_single_register(slave_id, write_addr, data_array, registers_array)
 * Write a single int val into a single holding register of the slave. 
int write_single_register(unsigned char slave,
        unsigned int write_addr, unsigned char *query, int *regs) 
        unsigned char function = FC_WRITE_REG; /* Function: Write Single Register */
        int status = 0;
        unsigned int reg_val;
        reg_val = query[REGS_H] << 8 | query[REGS_L];
        build_write_single_packet(slave, function, write_addr, reg_val, packet);
        regs[write_addr] = (int) reg_val;
        written.start_addr=write_addr;
        written.num_regs=1;
        return (status);
 * 	read_holding_registers(slave_id, first_register, number_of_registers,
 * registers_array)
 * reads the slave's holdings registers and sends them to the Modbus master
int read_holding_registers(unsigned char slave, unsigned int start_addr,
unsigned char reg_count, int *regs) 
        unsigned char function = 0x03; 	/* Function 03: Read Holding Registers */
        int packet_size = 3;
        int status;
        unsigned int i;
        unsigned char packet[MAX_MESSAGE_LENGTH];
        build_read_packet(slave, function, reg_count, packet);
        for (i = start_addr; i < (start_addr + (unsigned int) reg_count);
	       i++) {
                        packet[packet_size] = regs[i] >> 8;
                packet_size++;
                packet[packet_size] = regs[i] & 0x00FF;
                packet_size++;
        status = send_reply(packet, packet_size);
        return (status);
        Serial.begin(baud);
        switch (parity) {
        case 'e': // 8E1
                UCSR0C |= ((1<<UPM01) | (1<<UCSZ01) | (1<<UCSZ00));
                //      UCSR0C &= ~((1<<UPM00) | (1<<UCSZ02) | (1<<USBS0));
                break;
        case 'o': // 8O1
                UCSR0C |= ((1<<UPM01) | (1<<UPM00) | (1<<UCSZ01) | (1<<UCSZ00));
                //      UCSR0C &= ~((1<<UCSZ02) | (1<<USBS0));
                break;
        case 'n': // 8N1
                UCSR0C |= ((1<<UCSZ01) | (1<<UCSZ00));
                //      UCSR0C &= ~((1<<UPM01) | (1<<UPM00) | (1<<UCSZ02) | (1<<USBS0));
                break;                
        default:
                break;
        if (txenpin > 1) { // pin 0 & pin 1 are reserved for RX/TX
                Txenpin = txenpin; /* set global variable */
                pinMode(Txenpin, OUTPUT);
                digitalWrite(Txenpin, LOW);
        return;
 * update_mb_slave(slave_id, holding_regs_array, number_of_regs)
 * checks if there is any valid request from the modbus master. If there is,
 * performs the action requested
unsigned long Nowdt = 0;
unsigned int lastBytesReceived;
const unsigned long T35 = 5;
        unsigned char query[MAX_MESSAGE_LENGTH];
        unsigned char errpacket[EXCEPTION_SIZE + CHECKSUM_SIZE];
        unsigned int start_addr;
        int exception;
        int length = Serial.available();
        unsigned long now = millis();
        if (length == 0) {
                lastBytesReceived = 0;
                return 0;
        if (lastBytesReceived != length) {
                lastBytesReceived = length;
                Nowdt = now + T35;
                return 0;
        if (now < Nowdt) 
                return 0;
        length = modbus_request(slave, query);
        if (length < 1)
                return length;
        exception = validate_request(query, length, regs_size);
        if (exception) {
                        build_error_packet(slave, query[FUNC], exception,
                        errpacket);
                        send_reply(errpacket, EXCEPTION_SIZE);
                        return (exception);
        start_addr = ((int) query[START_H] << 8) +
                      (int) query[START_L];
        switch (query[FUNC]) {
                case FC_READ_REGS:
                        return read_holding_registers(slave, 
                        start_addr,
                        query[REGS_L],
                        regs);
                break;
                case FC_WRITE_REGS:
                        return preset_multiple_registers(slave,
                        start_addr,
                        query[REGS_L],
                        query,
                        regs);
                break;
                case FC_WRITE_REG:
                        write_single_register(slave,
                        start_addr,
                        query,
                        regs);
                break;                                
unsigned int CRC16, SEED, GP; //for CRC16
#define SEED 0xFFFF  //initialization for CRC16
#define GP   0xA001  //generating polynomial
int in_buffer[8]; // receiving buffer
#define CycleStart 2;  //MOD:0-P2
#define FeedHold 3;  //MOD:0-P3
#define StopFile 4;  //MOD:0-P4
#define SingleStep 5;  //MOD:0-D3
#define ResumeFile 6;  //MOD:0-D4
#define ZeroX 7;  //MOD:0-D5
#define ZeroY 8;  //MOD:0-D6
#define ZeroZ 9;  //MOD:0-D7
/// ----------------------- Functions -----------------------
void Reply_Inputs()
   CRC16 = SEED;
   int Inputs[] ={0x01, 0x04, 0x0A, 0x00, 0x00,
                  0x00, 0x00, 0x00, 0x00, 0x00,
                  0x00, 0x00, 0x00, 0x00, 0x00};
   Inputs[4] = ( 
               ((!digitalRead(9))<<7) | 
               ((!digitalRead(8))<<6) | 
               ((!digitalRead(7))<<5) |
               ((!digitalRead(6))<<4) |
               ((!digitalRead(5))<<3) |
               ((!digitalRead(4))<<2) |
               ((!digitalRead(3))<<1) |
               ((!digitalRead(2))   ) );
   for (int i = 0; i < 13; i++)
        Calc_CRC(Inputs[i], &CRC16); 
        Inputs[13]=CRC16;
        CRC16=CRC16>>8;
        Inputs[14]=CRC16;
   for (int i=0; i < 15; i++) Serial.write(Inputs[i]);
void Reply_Error()
   int Error[] ={0x01, 0x84, 0x00, 0x43, 0x00};
   for (int i=0; i < 5; i++) Serial.write(Error[i]);
void Calc_CRC(unsigned char b, unsigned int* CRC)
   int carry, i;
   CRC[0] ^= b & 0xFF;
   for (i=0; i<8; i++)
      carry = CRC[0] & 0x0001;
      CRC[0]>>=1;
      if (carry) CRC[0] ^= GP;