I have been running my machine several years, including yesterday.  Now I get the emergancy mode active, external estop requested.  I have changed the backup file to several days ago, to no effect.
Help please
Jay
  •  9,195 9,195
Re: emergancy mode active
« Reply #1 on: March 19, 2017, 02:22:11 AM »
First step would be to thoroughly check your inputs wiring and EStop / Home / Limit switches.
« Reply #2 on: March 19, 2017, 08:19:20 AM »
I have tried each one by disconnecting the wire one by one, and will try again by disconnecting them all.
Jay
  •  9,195 9,195
« Reply #3 on: March 19, 2017, 08:25:51 AM »
Hi Jay,
Home / limit switches are generally 'normally closed contact' and wired in series - perhaps yours are wired differently ?
Sometimes mechanical switches go bad and tapping them gently with a screwdriver handle can reveal a problem.
« Reply #4 on: March 19, 2017, 08:54:57 AM »
With all input pins disconnected, no change.  Still get emergancy mode and external estop requested.  What is a external estop?
Jay
  •  9,195 9,195
« Reply #5 on: March 20, 2017, 02:09:33 AM »
Hi Jay,
Are your switches wired as 'normally closed contact' ?
If your switches are 'normally closed contact' and wired in series then disconnecting them is of no help - they must be connected and producing a closed circuit.
Use a multimeter and check your Estop switch ...
Is it closed circuit ?
Press the switch - is it open circuit ?
Release the switch is it closed circuit again ?
Check your other switches the same way.
« Reply #6 on: March 20, 2017, 09:03:49 AM »
Thank you,  one of the limit switches got nocked out of adjustment and was open when it should have been closed.